A very controversial subject, pros and cons.
But yes, if the manufacturer says CaCl then you should do it. Although some say you can do both.
Personally I like to know whats coming out of the surface and a CaCl tells you that, but not a Rh test. Rh tells you what potentially might come out of the surface but there is no correlation between the two tests. Rh only tells you what the relative humidity is in the concrete. And they all can change if there is no barrier under the slab. So if you did not test prior to the installation there is no way to tell if the slab was beyond specs at that point in time.
Porosity, surface structure (steel troweled) and admixes have a huge bearing on what comes out of a slabs surface.
The inspector should grind the concrete surface 24 hrs prior to setting the CaCl tests. If doing a Rh test he should have documentation that his reusable probes have been re-calibrated in the last month. But if using the Rapid Rh probes re-calibration is not required.
I think your info might be off a bit. An Rh test (reusable) can be read an hour or so after the probe is set as it needs time to equilibrate. But not a Rapid Rh, it can be read in minutes. It's the CaCl test that must be read BEFORE 72 hours. Of course you can read the Rh test anytime after the initial equilibration time, even weeks or months for that matter.
But here's the kicker, a resuable probe reads from the top of the hole to the bottom. In a normal sized slab the depth is an inch and a quarter or so. The Rapid Rh probe only reads at that depth....below the probes bottom. There fore IMHO re-usable probes are deficient in that they read the rh at the top to the bottom of the hole giving you a potentially skewed result. Or an average if you will.