stewcom wrote:
I purchased 3000 sq ft of Bellawood Chestnut 3/8 from Lumber Liquidators and had it installed by their recommended installer in June, 2013. I spent over $25K including installation. It was installed over concrete slab and slab over grade. The sales person recommended glue down method over troweled- on underlayment. The floor started buckling and cracking a month later. Lumber liquidators admitted faulty installation and agreed to replace but will not back up any further problems. The same installer will be doing the warranty work. New moisture tests were done as follows:
TEST PLOT #1 4.98 lbs
TEST PLOT #2 3.62 lbs
TEST PLOT #3 5.59 lbs
TEST PLOT #4 2.57 lbs
TEST PLOT #5 2.42 lbs
TEST PLOT #6 5.59 lbs
The flooring we would like to install is a Bellawood Hardwood in chestnut. The installer has recommended two different methods of installation with the moisture conditions we have. They are as follows,.
•Floating floor using an Elastilon and 6mil vapor barrier product.
•Floating floor using a 3/4" CDX subfloor. The installer has not given me any specifics as to what he would use. I did some searching online and I found a subfloor component list that someone posted in a forum. Here is what they said to use.
-------------------------------------------------------------------------------------------------------------------------------
Level and patch concrete as needed.
6mm vapor barrier
Layer of 15# felt or similar
2 layer of 3/8 cdx grade plywood glued and stapled to each other. Run the sheets opposite direction of each other.
15#felt or similar.
Then install your hardwood using 1-1\2" staples...
This is for solid 3/4"
-------------------------------------------------------------------------------------------------------------------------------
At this point I am looking for a recommendation of what to use for a hardwood floor on concrete with moisture. I am not 100% sold on Elastilon as I feel that this product benefits the installer and not necessarily the person buying the wood. Harder to replace planks in the future. I know with hardwood this should not happen,. but in case of a moisture problem due to whatever I can't think of,. replacement would be easier I would think with a nail down method.
Could you pass this message on or let me know who I might be able to talk to for a second opinion on what I should do moving forward? The installer is leaving it in my hands to make a decision which is critical because they will not warranty any problems in future. Any help in making our decision would be much appreciated. Thanks!
First off, they should be running some ASTM F-2170-11 rh probes instead of CaCl ASTM F-1869-11 tests or even better both.
For floating plywood substrate and patch to flatten to spec, apply Bostick's MVP4, then poly, then 15 lb felt, then ply, then 15 lb felt again, then wood.
Installers cannot just lay any future warranty problems on you. They must approve or deny. If they approve then they are responsible. Don't believe any bull that these schisters are giving you.