NWFA Technical Bulletin C200 states Squeaky/Loose Floors ("Popping")
Cause:
• Movement of the wood flooring system, subfloor system or underfloor supports.
NWFA states OSB exposure 1 16" joists = nominal 3/4" thickness
NWFA states OSB exposure 1 16" up to 19" joists = nominal 3/4" glued and mechanically fastened.
NWFA states OSB exposure 1 Over 19.2" 1" glued and mechanically fastened or two layers of subfloor.
Research by Virginia Tech Institute states once OSB gets wet and dries the holding power is dramatically reduced. Moisture and OSB are a bad mix. Most installers have a dim view of osb as a nailing surface for hardwood floors. Yes code allows it BUT it also allows FHA carpet which Bob Shaw of Shaw Industries has stated that it is good for 6 months. You figure it out as regards code. Code is the bare minimum allowed.
Installing hardwood parallel to the flooring joists is a clear violation of all manufacturing guide lines that I have ever seen or heard about. This is a first for me!
• Improper nailing and nailing position.
• Cracked tongues. ½” staples will act like a wood chisel and split tongues.
• Mixing cleats and staples is a definite no no.
• Flooring installed with an excessively high moisture content or over a subfloor with excessive moisture. See comment above regarding osb and moisture.
• Foudation settlement or subfloor movement.
• Improper subfloor materials that will not hold nails. See Comment above osb.
Additionally I have inspected floors that are not securely fastened to the subfloor i.e. gaps between the subfloor and the hardwood. Easily detected by tapping with a hammer and listening for hollow sounding areas compared to areas that do not. Generally next to walls etc will produce sounds associated with no gapping between the subfloor and the hardwood. When they pulled those boards they should have used a taper guage and measured the distance between the hardwood and osb. I’m guessing it it substantial.
All you OSB advocates out there take some osb and nail some hardwood and then inspect the backside and note the amount of blowouts due to the voids in osb.
Most Manufacturer’s state 35% to 55% and NWFA states 30% to 50% so this inspector saying 36% is incorrect only shows ignorance of his own mfg guidelines besides the issue appears to be subfloor movement not abnormal gapping.
It has been stated that too many inspectors, which certification they possess who knows, want to throw installers under the bus however this installer needs to to a few NWFA classes and get certified if he wants to continue in this business. Go to
www.nwfacp.org and get a nwfa certified inspector his report you can take to court as a expert witness and IF you feel he hasn’t given a proper report can contact the NWFA for a review as to the correctness of the report. Though the builders one year warranty may be up his responsibility has not in a court of law if he contracted the installer and then stonewalled you for a solution..
Hope this helps!