KevinD wrote:
Do you not run the a/c? If you have that high of r/h your a/c isnt cycling properly. sounds like its short cycling. 85% rh is like a sauna and is odd in an occupied space. Most concrete m/c test give you a measure of #'s per sf . The r/h is going to change constantly throughout the day as the outside temps change.
KevinD, we run the AC and the house is at 76 degrees constantly. My humidity meter of the house is between 45% and 58 to 60%. 85% RH is the reading from the Wagner RH in-situ testing that we performed IN the concrete slab. The calcium chloride test we have not done since it is not accurate over cutback/black mastic residue.
I just got a call back from Mirage and said they have no problem using a pad that is not theirs as long as...
It is less than or equal to 3.5mm thick
Its Compressibility at 25% deflection rating is greater than or equal to 8psi when dealing with 2.6 to 3.5mm thick pad
It also must have a water vapor transmission of less than or equal to 0.6 lb / 1,000 sq. ft. / 24 hrs
They stated if I have higher than normal moisture readings to lay 6 mil poly or 10 mil poly under the pad that meets the min specs listed above.