Both NOFMA and the NWFA recommend no more than a 2% variance in the moisture content between the subfloor and SOLID (not engineered) plank flooring. With solid strip flooring, a 3 to 4% moisture content variance is supposedly allowed. IMO, any wood subfloor at 12% MC and over is suspect and will probably cause problems. This is from NOFMA's Installation Manual:
http://www.nofma.org/Portals/0/Publicat ... Floors.pdf
"The average moisture content
of framing members and subflooring should be
below 12%-14% before delivery of the flooring. Moisture
contents above 12%-14% can cause moisture related
problems."
NOTE: It says below 12 to 14%. Not 12 to 14% is OK. Big difference.